Hi Everyone, I have a sofar solar HYD6000-EP, the communication between esphome-jk-bms-can and the inverter works perfectly but my issue is that I only have bulk phase and wait phase. It never goes to absorption phase, at least that is what I see in home assistant. Do you have an idea on why ? Thank you for your help. |
Beta Was this translation helpful? Give feedback.
Replies: 2 comments 6 replies
-
Hi, I have found the reason. The jk-bms makes a wrong estimation of the SOC at 99% and the inverter stops charging (there might be internal rule to stop charging at 99%). If I reset the capacity of the jk-bms the soc get lower and charging starts again. Don't know what to do with that for the moment... |
Beta Was this translation helpful? Give feedback.
-
Please consider supporting my work so I can continue to develop new feature and provide help and assistance. |
Beta Was this translation helpful? Give feedback.
It is constant current to the Absorption voltage, where it tapers off and becomes constant voltage.
This is my constant charging current as it approaches the absorption voltage.